So have a bit of an issue at the job I'm on. There are 8, 4" EMT runs entering a box.
However, there are only 3, 4" EMT exiting it at the back (opposite the cover) and going up through the ceiling about 2.5ft to another box, then to the switchgear. These holes were drilled in the concrete (x-rayed for PT cables) months ago.
In each of the 8 incoming 4" conduits are 4 350kcmil aluminum THHN conductors and a #2 (I think) ground.
The individual who had the holes drilled saw the table in NEC that said 4" EMT could hold 11 350kcmil conductors and assumed because 11 x 3 = 33, this should be enough.
Since 11 isn't a multiple of 4, however, that means that not all of the circuits will be able to stay together.
My Southwire Conduit Fill app says 4" EMT can hold 12 conductors before hitting 40% Fill.
1) Why the discrepancy between NEC and Southern and who go believe?
2) How screwed are we? What other problems might there be? The feeders have been pulled and if we have to remove the box, we have to pull them out.
However, there are only 3, 4" EMT exiting it at the back (opposite the cover) and going up through the ceiling about 2.5ft to another box, then to the switchgear. These holes were drilled in the concrete (x-rayed for PT cables) months ago.
In each of the 8 incoming 4" conduits are 4 350kcmil aluminum THHN conductors and a #2 (I think) ground.
The individual who had the holes drilled saw the table in NEC that said 4" EMT could hold 11 350kcmil conductors and assumed because 11 x 3 = 33, this should be enough.
Since 11 isn't a multiple of 4, however, that means that not all of the circuits will be able to stay together.
My Southwire Conduit Fill app says 4" EMT can hold 12 conductors before hitting 40% Fill.
1) Why the discrepancy between NEC and Southern and who go believe?
2) How screwed are we? What other problems might there be? The feeders have been pulled and if we have to remove the box, we have to pull them out.