Can you put fiber optic inside a conduit with conductors????
It always amazes me that people want to leave a rope or string in an occupied raceway for later use. In most cases this will not be successful for later use and almost always damages existing conductors.
Work for a company that always wants and requires string (jetline) in any conduit that goes underground. Spare or used, doesn’t matter.It always amazes me that people want to leave a rope or string in an occupied raceway for later use. In most cases this will not be successful for later use and almost always damages existing conductors.
While I don't know of any code violation to install a rope or Jetline, I would try to discourage the practice. That said, if it is gonna be done I would require the fill calc to include the rope as the code requires all conductors to be counted as fill (not just CCCs) so it would seem reasonable that it should apply to anything occupying space. A piece of Jetline I would be inclined to ignore.@texie, you are an inspector so what would you require? A calculation based on the rope size or none at all?
If we have to count a normally non-current carrying equipment grounding conductor in on fill calculations one would think, a rope Or any other object taking up space would have to be calculated in as well.@texie, you are an inspector so what would you require? A calculation based on the rope size or none at all?
that would be logic though. if the code does not actually require it, it is not required.If we have to count a normally non-current carrying equipment grounding conductor in on fill calculations one would think, a rope Or any other object taking up space would have to be calculated in as well.
that would be logic though. if the code does not actually require it, it is not required.
optical fibers have to be counted because chapter 9 table 1 says so.
(5) For conductors not included in Chapter 9, such as multiconductor
cables and optical fiber cables, the actual
dimensions shall be used.
I can't find anything anywhere in the code that thinks someone would leave a rope in a conduit. Maybe that is prohibited.
That said, if it is gonna be done I would require the fill calc to include the rope as the code requires all conductors to be counted as fill (not just CCCs) so it would seem reasonable that it should apply to anything occupying space. A piece of Jetline I would be inclined to ignore.
It's a conductor because the code says it's a conductor.Is there an obscure definition that considers fiber optic lines to be "conductors". Because fiber optic lines are made out of glass, which is an insulator. And so would a pull string be an insulator.
It's a conductor because the code says it's a conductor.
Although it is a conductor that doesn't (or isn't intended to conduct normally) conduct, there is often a steel strand for structural and location purposes.It's a conductor because the code says it's a conductor.
Although it is a conductor that doesn't (or isn't intended to conduct normally) conduct, there is often a steel strand for structural and location purposes.