shamrock12
Member
- Location
- Upstate NY
Suppose you have a typical underground feeder run where you would use schedule 40 RNC for the underground portion, but uses schedule 80 RNC where both ends of run goes above ground and is subject to physical damage. Is there an exemption in NEC that would allow you to use the maximum allowable conduit fill of schedule 40 for the entire run (up to a certain length)?
The schedule 80 at both ends of run would act as sleeves to protect the conductors from physical damage like lawn mower, weedeater, etc. Typically those "sleeves" would be about 6 feet each in length (4-1/2 feet above ground and 1-1/2 feet below ground straight down to 90* elbow).
The schedule 80 at both ends of run would act as sleeves to protect the conductors from physical damage like lawn mower, weedeater, etc. Typically those "sleeves" would be about 6 feet each in length (4-1/2 feet above ground and 1-1/2 feet below ground straight down to 90* elbow).