Note 9 of Ch.9 states to treat the cable as one conductor.
When doing conduit fill calculation say for (2) 12-2 NM cables, the two cables are considered as (2) individual conductors and use the 31% column or treated as 4 conductors and use the 40% column?
TIA
Each separate cable gets treated as a single conductor. So with 2 cables you would calculate area as 2 individual conductors. The conduit is going to get big fast.
Say for 12/2 NM-B cable you would calculate conduct fill as if you had two conductor each 0.4" in diameter.
so you would use the 31% column to calculate the fill?
Yes, if you had one cable it would be 53% fill. More than 2 cables 40%. Raceway 24" or less 60%.
For 2 conductors in general, this is a blindspot in the NEC, since two circles have a lot of empty space when packing in another circle, and that's where the 31% special case comes from. Following the logic of the 60% rule, I estimate that the equivalent limit for 2 wires should be around 45%.
The general rules are about 75% diametral fill, and the 60% rule is about 90% diametral fill for 3+ wires. So 2 wires would have this diametral fill at 45%.
What about oval packing? If you can still meet the 60% rule with just 2 oval-shaped cables, go for it. The fact that ovals pack better than circles, should allow you to take full credit for the 60% nipple rule. In a longer raceway, you have a lot less control over how they arrange, so in that case, you account for the full virtual circle of the larger "diameter" of the oval.