conduit fill for SA cable

relbas

Member
I need direction to locate a conduit fill chart for SA cable? I need to run a wire inside the sauna and I am planning to use High temperature liquid seal flexible conduit.
1734438255031.png
 
It's a silicone cable 310.15(B)(18). I don't know of any table in annex C that includes it.
 
I would treat the cable as one conductor. Calculate your fill at 53% and contact the cable manufacturer to obtain its approx. area in sq. in.
 
I am planning to use this cable because the rating is 200* C and it is going in to feed the sauna.
The typical temp inside the sauna is over 90* C so I am getting the seal tight that rated over 90* and this is the only high temp wire that I can get.
Am I thinking correctly or I am missing something?
 
Last edited:
I am planning to use this cable because the rating is 200* C and it is going in to feed the sauna.
The typical temp inside the sauna is over 90* C so I am getting the seal tight that rated over 90* and this is the only high temp wire that I can get.
Am I thinking correctly or I am missing something?
What kind of sauna has an operating temperature over 90° C?
 
HUUM is the manufacture name and they are claiming that the temperature inside the room can reach 180 and above.
 
HUUM is the manufacture name and they are claiming that the temperature inside the room can reach 180 and above.
90° C = 194° F so it should be okay. Are you actually running the wires inside of the sauna?
 
That sounds like an over rather than a sauna. I have read you can slow roast a turkey at 80 C.
 
90° C = 194° F so it should be okay. Are you actually running the wires inside of the sauna?
Yes it looks like a cocoon filled with stones in the corner of the room and the space about 3’ to the closest wall. I am afraid that the liquid tight will not handle the temperature
so the #8 thhn with the temperature correction is about 40 Amp?correct
 
90° C = 194° F so it should be okay. Are you actually running the wires inside of the sauna?
Yes it looks like a cocoon filled with stones in the corner of the room and the space about 3’ to the closest wall. I am afraid that the liquid tight will not handle the temperature
 