Conduit fill issue

Status
Not open for further replies.

rhaneberg

Member
Location
Fostoria Ohio
Occupation
Retired
I want to run a circuit for electric car charging from my house to my unattached garage in underground in schedule 80 pvc conduit. At 50 amps I must use # 6 Awg conductors. But since the 240 load is almost entirely balanced then must the neutral and ground be the same wire gage as the 240 volt conductors?
 
Your profile says you occupation is "retired". What are you retired from?
If you were never in the electrical trade Forum rules do not allow us to help you with a DIY project.
 
Let him look up the EGC in Table 250.122
Let him ask the inspector about the neutral
 
I am closing this thread, in accordance with the Forum’s rules.

This site is designed for:

Contractors
Electricians
Engineers
Inspectors
Instructors
Other electrically related individuals
This NEC Forum is for those in the electrical and related industries.

Forum rules prohibit us from assisting a person to perform or assist others to do electrical work who are not qualified. The reason is that the forum’s owner does not want a person to get an answer to the question they asked, but not get answers to the other questions they should have asked and were unaware they needed to ask. Mike Holt Enterprises and the Moderators of this Forum do not wish to place you and your family in danger, by allowing others to give you too little information to ensure that the installation is safe
 