I've got 1" EMT attached to the panel with appx 20 or so THHN 12 guage wires coming in. Inspector said that was "too many" and that I have to derate or remove some of the wires from the conduit.
Annex C of 2008 NEC shows I can have up to 26 12 AWG THHN conductors in a 1" EMT....BUT...table 310.15(B)(2)(a) states that I'd have to derate the conductors to 50% (this is assuming I actually have 20 conductors, I didn't count them yet.)
So how do I reconcile these two tables? And does this mean that if I were to have a 3" EMT with 4-6 conductors that I would STILL have to derate them to 80%??? :blink:
Can I show the inspector Annex C and say I'm ok? What if he shows ME table 310.15(B)(2)(a)?
Thanx for your help.
Zeno
Annex C of 2008 NEC shows I can have up to 26 12 AWG THHN conductors in a 1" EMT....BUT...table 310.15(B)(2)(a) states that I'd have to derate the conductors to 50% (this is assuming I actually have 20 conductors, I didn't count them yet.)
So how do I reconcile these two tables? And does this mean that if I were to have a 3" EMT with 4-6 conductors that I would STILL have to derate them to 80%??? :blink:
Can I show the inspector Annex C and say I'm ok? What if he shows ME table 310.15(B)(2)(a)?