Conduit Fill Rules for TC Cable

Status
Not open for further replies.

Saturn_Europa

Senior Member
Location
Fishing Industry
Occupation
Electrician Limited License NC, QMED Electrician
I am running a circuit to a HVAC condenser unit. Its a 26 FLA demand and a 300' run. The manual said maximum voltage drop is 2%. My plan was to run the wire in a cable tray, then transition to 1" ridged aluminum conduit for the outside of building. Due to the voltage drop I will have to run 6/2 with a ground TC cable. I will also have to run 12/2 with ground TC cable for my convenience outlet. Are there special rules for conduit fill when it comes to TC cable?
 
I am running a circuit to a HVAC condenser unit. Its a 26 FLA demand and a 300' run. The manual said maximum voltage drop is 2%. My plan was to run the wire in a cable tray, then transition to 1" ridged aluminum conduit for the outside of building. Due to the voltage drop I will have to run 6/2 with a ground TC cable. I will also have to run 12/2 with ground TC cable for my convenience outlet. Are there special rules for conduit fill when it comes to TC cable?

as far as I can tell if you can jam it in the tube it is probably OK.
 
I am running a circuit to a HVAC condenser unit. Its a 26 FLA demand and a 300' run. The manual said maximum voltage drop is 2%. My plan was to run the wire in a cable tray, then transition to 1" ridged aluminum conduit for the outside of building. Due to the voltage drop I will have to run 6/2 with a ground TC cable. I will also have to run 12/2 with ground TC cable for my convenience outlet. Are there special rules for conduit fill when it comes to TC cable?

Essentially, when you put multiconductor cables in a conduit, you treat them as if each cable were a perfect circle with a diameter equal to the largest possible diameter (if there is an ovalish shape to the cable). And then you apply the standard 53%/31%/40% rules. Or 60% if it is 2 ft and less.
 
Depends on the TC cable. Many TC power cables run all the same size conductors and no downsized EGC.

I don't see a lot of larger TC but I can't recall ever seeing one with a smaller EGC in it, but maybe my memory is confused. I don't recall for sure but I also seem to recall the grounds are usually bare, but I might be remembering funny about that too.
 
I don't see a lot of larger TC but I can't recall ever seeing one with a smaller EGC in it, but maybe my memory is confused. I don't recall for sure but I also seem to recall the grounds are usually bare, but I might be remembering funny about that too.
I'm aware w/G is available, but I've never seen a Type TC power cable with a designated EGC.
 
We pulled in almost 9,000' of tray cable at a mill in washinton, each one had 3 (three) 500MCMs with a 250 gnd (insulated)! But it was aluminum, not as hard a job as it sounds:)
 
Now that we have told you how to build the clock, we might tell you the time :)
IN answer to your original question, see Note 9 in the Notes to Table 9 where you will find a multi-conductor cable is treated as a single conductor in determining conduit fill. Determine the area of your cable and check the Table a single conductor of the same area.
 
Now that we have told you how to build the clock, we might tell you the time :)
IN answer to your original question, see Note 9 in the Notes to Table 9 where you will find a multi-conductor cable is treated as a single conductor in determining conduit fill. Determine the area of your cable and check the Table a single conductor of the same area.

6/3 TC cable has an outside diameter of 0.69

In order to save space, I was going to change out the 12/3 with 14/2 and use the ground in the 6/3 for the outlet and HVAC system. I am pretty sure I can do this because both circuits will originate at the same panel.

14/2 TC cable has an outside diameter of 0.34

This puts the conduit fill at 51%. So it looks like I will have to upsize my conduit.

When I called the supply house, they didnt have 6/2 with ground only 6/3 in red, black, and blue. There is an exception for the EGC to be marked green when its part of a multiwire cable, installed in an industrial setting that is only accessible to qualified individuals.
 
I'm aware w/G is available, but I've never seen a Type TC power cable with a designated EGC.

I agree that most of the ones I have seen that are smaller (< 10 awg) all the conductors typically are insulated. I was referring to larger ones, not that I have seen very many of them.

I don't know if the larger cables typically come with full size grounds or not. I think you can pretty much get whatever you want these days. Sometimes it is pretty cost effective to get only what you need.
 