In general it’s not allowed to run low-voltage wiring along with line voltage in the same conduit. However, it seems to be permissible to put another conduit in the conduit through which to run the low voltage wiring.
Example: 1-1/4 EMT with 3 THHN wires and one 1/2 ENT. Through the ENT Ethernet.
How does conduit fill work in this case?
Here is my attempt: 1-1/4 EMT has 1.23sqin cross section. 1/2 ENT has 0.196sqin.
Now I subtract them and the remaining area in the EMT is 1.031sqin which corresponds to 1.15” diameter. Round down to an 1” EMT. In a 1” EMT I could run up to four AWG4 THHN copper.
Is that right?
Example: 1-1/4 EMT with 3 THHN wires and one 1/2 ENT. Through the ENT Ethernet.
How does conduit fill work in this case?
Here is my attempt: 1-1/4 EMT has 1.23sqin cross section. 1/2 ENT has 0.196sqin.
Now I subtract them and the remaining area in the EMT is 1.031sqin which corresponds to 1.15” diameter. Round down to an 1” EMT. In a 1” EMT I could run up to four AWG4 THHN copper.
Is that right?