E eesonny Member Oct 31, 2013 #1 Can I install 3-1/0 3/C cables in a 4" RGS conduit for a 300 hp motor? Or will there be issues with heat generated in the conduit?
Can I install 3-1/0 3/C cables in a 4" RGS conduit for a 300 hp motor? Or will there be issues with heat generated in the conduit?
roger Moderator Staff member Location Fl Occupation Retired Electrician Oct 31, 2013 #2 I must ask why you are asking this question? Roger
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 31, 2013 #3 No, your wire is too small for that application. Assuming a 3 phase 480 volt motor, you would need conductors with an ampacity of 451 amps. Your proposed installation has an ampacity of 357 amps.
No, your wire is too small for that application. Assuming a 3 phase 480 volt motor, you would need conductors with an ampacity of 451 amps. Your proposed installation has an ampacity of 357 amps.