Installation Suggestions
This chart is based on the maximum number of cables permitted in conduit under the National Electric Code, and is calculated on the area of the cables with 40% of the conduit filled. *For conduit runs of 50 to 100 feet, the installed number should be reduced by 15%, or use the next size larger conduit. Each 90? conduit bend may be estimated as equal to the friction of 30 feet of straight level conduit. If more than two 90? bends are to be used in the conduit run, or if the run is to be over 100 feet in length, insert a pull box. The use of anti-friction agents is recommended during pulling operations.
Caution: Be sure the anti-friction agent selected is compatible with the cable jacket material. (Check the label.)