E enireh Senior Member Location Canyon Lake,TX Dec 30, 2016 #1 will 3 - 4/0's, #4, 3 -2/0's, #8 thhn fit nice in 3" pvc?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Dec 30, 2016 #2 You're allowed 6-#4/0 in a 3" Sch40 PVC. Might make it.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Dec 30, 2016 #3 Unless I made a math mistake, no problem
J JFletcher Senior Member Location Williamsburg, VA Dec 30, 2016 #4 augie47 said: Unless I made a math mistake, no problem Click to expand... same.