Where am I making my mistake ?
Given 3" Sch 80 PVC and 600kcmil Cu.
I was asked how large a conductor I could add given 3 conductors in the conduit.
Table C9 shows 3 600 kcmils allowed in a 3" Sch 80 but when you go back and do the math using Chapter 9, (3) 600 kmil THWNs have a combined area of 2.6028 which exceeds the Table 4, over 2 wire, available area of 2.577.