what size EMT for (4) 3/0 THHN, + 1/0 EQG, Cu ????
thank you
what size EMT for (4) 3/0 THHN, + 1/0 EQG, Cu ????
thank you
Bigger than 3/4"
Roger
It will fit in 4”
Or any EGC, for that matter.Not sure why you'd need a 1/0 EGC, though.
Or any EGC, for that matter.
You can skip the calculation by looking in Table C.1 in Annex C.
Another option, there is also this great thing called Google and the internet. Open your computing terminal, and type in "raceway fill calaculator" and I bet you a Reuben you will have multiple choices.
annex C is only if all the conductors are the same size
You can still use annex C in this particular case - just look at how many 3/0’s fit in a certain size.
the 1/0 could be for medical equipment or other equipment that asks for a larger than normal ground. Or maybe it’s 3/0 wire on something like a 20A breaker and everything is upsized for voltage drop.
You can still use annex C in this particular case - just look at how many 3/0’s fit in a certain size.
the 1/0 could be for medical equipment or other equipment that asks for a larger than normal ground. Or maybe it’s 3/0 wire on something like a 20A breaker and everything is upsized for voltage drop.
If it is a 20 amp circuit upsized for VD, then the EGC would also need to be 3/0...........
........Where might one need a 1/0 EGC with 3/0 ungrounded conductors? ..........