Dsg319
- West Virginia
- Wv Master “lectrician”
Yep, one of those strange but true quirks of the NEC.There is no "round up" unless the conductors are the same size.
I’ve got one as well, though we usually work off of a set of prints where everything is already figured out and we just gotta put it together. And had been a while since I’ve done a calculation and still nice to know In my head how to do on paper for my own sake lol.I use an online conduit-fill calculator.
If I understand your question correctly you could only add an additional 10awg of the same size with the fraction of 0.8 or greater.If you calculate a raceway can hold 6.7 conductors you are limited to 6 conuctors.
If you calculate a raceway can hold 6.8 or 6.9 conductors you can install 7.
different sizes just doesn't work out, If you have a 10 AWG and remaining room for 5.8 6 AWG's can you add an additional 6? an additional 10? This may seem simple but what if you have even more variety of sizes of conductors involved. Which one do you apply the fractional figure to when rounding up?
But unless they are all the same size how do you know which one of the sizes you can round up?If I understand your question correctly you could only add an additional 10awg of the same size with the fraction of 0.8 or greater.
If they are all the same size you are likely to use Table C which takes the .8 factor into consideration so it's kinda one of those nice thing s to know but useless![]()
Those tables are partially your fault? IMO all they do is add more pages to the book, I hardly have ever used them.Hey I worked hard on that table and it was a pain getting that .8 to work. I believe I started a thread on that and got help on that issue from Smart $... Now I feel useless...
Anyone that runs enough raceway knows how many 14, 12 and 10 fit in most 1/2 and 3/4 raceways off top of their head anyway and maybe a few other common conductor and raceway applications are stuck in their head as well. If anything varies from those usual applications, go to chapter 9 and figure it out. If not all same size you are using chapter 9 regardless.
He's so vain, he probably thinks that post is about him.Not everyone is as vain and as smart as you.
Thanks, I appreciate the helpful and atta boy compliments. Not everyone is as vain and as smart as you.