difowler1

Senior Member
I'm not finding pvc schedule 40 conduit size for 4/0 aluminum use-2 in the code book. I need 100 characters to post this, so here is some fill.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The only place I notice USE appearing in the Chapter 9 Table is in 5A where it accompanies RHW
From an earlier thread it was fairly well documented that most USE-2 was also rated RHW so you are probably safe using the RHW dimension.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The only place I notice USE appearing in the Chapter 9 Table is in 5A where it accompanies RHW
From an earlier thread it was fairly well documented that most USE-2 was also rated RHW so you are probably safe using the RHW dimension.
I agree and if it's not dual rated then it cannot enter the structure.
 