Dennis can you show the calculation?Yes, you can
I was already on it. ThanksDennis can you show the calculation?
You do know that you can use #3 for 80 amps if the load is not more than 75 amps or you can use #2 with 90 amp breakerThanks, I really appreciate you.
Sch80 will have less fill than Sch40.I noticed you are using alum. so that is usually xhhw-2????? If so that is a tad bit smaller so you are still good depending if I chose the correct insulations
The product standards show that the required insulation thickness for those wire types to both be 30 mils for 6 AWG, and show 2 THWN-2 as having 40 mils of insulation and 2 XHHW-2 as having 45 mils.Oddity,,,,
I did the math using XHHW-2 and exceeded the fill... #2 XHHW-2 is smaller than THWN-2, but #6 shows to be larger..... Not sure if there's a mistake in the Table or what ???
#2 .1146 X 2 = .2292
#.6 .0590 X 2 = .118
.2292 + .118 = .3472 1" Sch 40 = .333