Hello, I’m installing a Level 2 Electric Car charger. The max amp draw is 48 amps, so I’ll be installing a 60 amp 240 volt circuit. I’m going to use 2 #6 THHN with 1 #10 THHN for a ground. So I would need .122 of area in a 1/2 inch EMT (this will be all inside) once I completed the math I have .125 of fill area in the 1/2 inch, my question is, would .003 make a big differences. Reason for the 1/2 inch is the conduit will be installed in a finish basement so I was looking at trying to keep the conduit less obtrusive. As a side note I’ll be changing to 1/2 inch flex with has an area of .127 so we are good for flex. Thank You for your input on this matter.