Conduit Fill

Status
Not open for further replies.

HKYPLR

Member
Location
LONG ISLAND
I met a gentleman that says: that the equipment grounding conductor(s) do not count for conduit fill for the number of conductors in a conduit.
 
The words "conduit fill" pretty much sum up the counting of conductors. If it fills the conduit it counts. I hear this from time to time from other electricians too and wonder where they've learned this.:-?
 
I believe people get confused between conduit fill, where the EGC matters, and derating a certain number of current-carrying conductors, where it does not.
 
kc8dxx said:
I believe people get confused between conduit fill, where the EGC matters, and derating a certain number of current-carrying conductors, where it does not.


I believe you got it. Interesting that for box fill the EGC only counts once. Why is that-- 4 nm cables in a box and the EGC counts one time--hum.

No wonder everyone gets confused.
 
Pierre C Belarge said:
The reason is for pulling purposes, and potential damage for too many conductors.


What had pulling got to do with the number of EGC's in a box being counted as one? UR comfusing me Pierre.
 
Dennis Alwon said:
Interesting that for box fill the EGC only counts once. Why is that-- 4 nm cables in a box and the EGC counts one time--hum.
Probably because the EGC's don't contribute to heating; they merely take up space.
 