raydamesek
Member
I have six 20A 220V circuits to run. I want to put twelve #12 THHN conductors and one #12 THHN ground in Alflex conduit. I use a program that tells me that the fill for these 13 conductors is 28.70% for 3/4" conduit. (In practice I would use at least 1" conduit.) Since this fill is less than the 40% cited in Table 1 chapter 9, are there any other factors pertaining to derating of any sort that I should account for in the conduit. I'm not concerned with turns, boxes, etc. for this question.