PRODUCT MARKINGS
A circuit breaker that is Classified only is marked on the side with the
statement:
??Classified for use only in specified panelboards where the available
short-circuit current is 10 kA, 120/240 volts ac or less. Do not use in equipment
connected to circuits having an available system short-circuit current
in excess of 10 kA, 120/240 volts ac. For catalog numbers (or equivalent) of
specified panelboards, refer to Publication No.______ provided with this circuit
breaker. If additional information is necessary, contact [Classified circuit
breaker manufacturer?s name].??
A circuit breaker that is both Classified and Listed is marked on the side
with the statement:
??This circuit breaker is Listed for use in circuit breaker enclosures and
panelboards intended and marked for its use. This circuit breaker is Classified
for use, where the available short-circuit current is 10 kA, 120/240 V ac
or less, in the compatible panelboards shown in Publication No. ______ provided
with this circuit breaker. When used as a Classified circuit breaker, do
not use in equipment connected to circuits having an available system
short-circuit current in excess of 10 kA, 120/240 V ac. If additional information
is necessary, contact [Classified circuit breaker manufacturer?s name].??
The referenced publication is a compatibility list which tabulates the company
name, catalog number, number of poles and electrical ratings of the
Classified circuit breaker, in addition to the company name and catalog
number of the applicable UL Listed panelboards, and corresponding UL
Listed circuit breakers in place of which the Classified circuit breaker has
been investigated. The compatibility list also details the maximum permissible
voltage and maximum available short circuit current of the supply system
to the panelboard. The Classified circuit breaker is not suitable for the
specified application if the system supply characteristics exceed the maximum
values indicated in the compatibility list. One copy of the compatibility
list is provided with each circuit breaker.
Circuit breakers which are both Classified and Listed have markings as
above, with the addition of the Listing Mark, located on the side of the circuit
breaker.