laketime

Senior Member
We have a customer who has a back up generator, installed by another contractor. In the spring as the snow thaws the 2" conduit that feeds from the generator to the transfer switch starts pumping water in the transfer switch. Are there any products that are good at sealing the conduit at the entrance to the transfer switch or what methods have other used to stop this issue.
 

MAC702

Senior Member
Location
Clark County, NV
What's the rest of the story? How is the water getting into the conduit? Is it just a sleeve from a direct buried cable? Are there elevation differences causing this?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
We have a customer who has a back up generator, installed by another contractor. In the spring as the snow thaws the 2" conduit that feeds from the generator to the transfer switch starts pumping water in the transfer switch. Are there any products that are good at sealing the conduit at the entrance to the transfer switch or what methods have other used to stop this issue.

American Polywater. Here is a link to their sealants page: https://www.polywater.com/product-category/polywater-sealants-selection/
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In the past we have used potting compound that is typically used for wet niche pool lights.
 

laketime

Senior Member
What's the rest of the story? How is the water getting into the conduit? Is it just a sleeve from a direct buried cable? Are there elevation differences causing this?

It is N Idaho and wet ground. There is an elevation difference of about 5 feet. The conduit seems to be a complete run but who knows what is happening underground.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If the conduit enters the enclosure from below, you might consider putting a drain fitting on the conduit below the height of the enclosure. The problem will be to do that in a way that is NEC compliant.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If the conduit enters the enclosure from below, you might consider putting a drain fitting on the conduit below the height of the enclosure. The problem will be to do that in a way that is NEC compliant.
How about a T-condulet with a perforated drain cover in the bottom leg?
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
Having experienced a “fountain conduit” myself due to an elevation difference from a pad transformer to house meterbase years ago before “slip riser fittings” existed.

Install a slip riser fitting (not an expansion coupling) it has enough space between sections to allow the water to drain before it reaches the height of your transfer switch. Unless the flow rate is to great.

Also, if memory serves me right the NEC allows up to 1/4” hole to be drilled into equipment to allow for drainage.
 

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
Breather Kit (SDA Series) - Hammond Mfg.
Look around I typed in electrical enclosure drain, there were other types.
 

kwired

Electron manager
Location
NE Nebraska
Is there standing water around generator and it leaks into conduit, or worse yet into other equipment at the generator end of the run?

I'd try to minimize that first, if you successfully plug the conduit you might only be solving one part of your problem.
 

Wire-Smith

Senior Member
Location
United States
Quazite box in low spot of underground run near generator, put break in conduit there use endbells on conduit and keep them running straight through, bonding jumper if conduit is mettalic.
 