C casey1234 Member May 25, 2005 #1 Is it ok to run EMT conduit with compression connectors in a classified area (Class 1 Div 2)? The area is a storage room inside a building. The conduits pass through this area and are sealed where they enter and exit the room.
Is it ok to run EMT conduit with compression connectors in a classified area (Class 1 Div 2)? The area is a storage room inside a building. The conduits pass through this area and are sealed where they enter and exit the room.
ryan_618 Senior Member Location Salt Lake City, Utah May 25, 2005 #2 Re: Conduit in Class 1 Div 2 Area No. See 501.10(B)(1).