Conduit in Concrete

Status
Not open for further replies.
Location
Denver, CO
Occupation
Electrical/Lighting Engineer
I am designing a snowmelt system using MI cable. To cross expansion joints I need to install the heat cable in a conduit. We cannot use PVC. Obviously typically all I use is PVC to bury conduit in concrete. But I cant in this case. Any recommendations as to what metallic conduit type is best fit to bury in concrete?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
What temperature does it need to withstand. Fiberglass conduit will take up to 250?F, I believe
 
Location
Denver, CO
Occupation
Electrical/Lighting Engineer
Looks like I should be just under 250 according to the manufacturers data. I mean just under. Too close for comfort unless its my only option.....
 

StarCat

Industrial Engineering Tech
Location
Moab, UT USA
Occupation
Imdustrial Engineering Technician - HVACR Electrical and Mechanical Systems
Common Refrigeration Method

Common Refrigeration Method

It is common practice in certain walk in freezer installations to run heat cable in EMT which will then be covered in concrete, but I would think rigid might be a better choice. This is usually done on the warm side of the door threshold and there is typically a spare cable added along with the one to be run.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
EMT?


Personally, I would be asking the heat cable manufacturer.

I don't get why it needs to be in conduit if it is MI.
Physical sleeving where it crosses the expansion joints and there could be relative motion?
Possibility of crush damage if concrete sections move vertically or horizontally?
 
Location
Denver, CO
Occupation
Electrical/Lighting Engineer
Correct, the conduit is at the expansion joints to keep the cable from breaking under shear force.

I talked to the manufacturer who said RMC works. It may crack a bit down the road but the cables remain protected.

I guess per the manufacturer I will specify RMC at the expansion joints.
 