conduit in extension boxs
irish
New member
on flush boxs or surface boxs with a extension box. can conduit be installed in the K.O.s of the extension? where in code book is this covered?
hornetd
Maryland
Journeyman Electrician, Retired
Re: conduit in extension boxs
314.22 Exposed Surface Extensions.
Surface extensions from a flush-mounted box shall be made by mounting and mechanically securing an extension ring over the flush box. Equipment grounding and bonding shall be in accordance with Article 250.
Exception: A surface extension shall be permitted to be made from the cover of a flush-mounted box where the cover is designed so it is unlikely to fall off or be removed if its securing means becomes loose. The wiring method shall be flexible for a length sufficient to permit removal of the cover and provide access to the box interior, and arranged so that any bonding or grounding continuity is independent of the connection between the box and cover.
roger
Fl
Retired Electrician
From Mike Holt
Roger