The first question we always get asked is “How deep do we bury the wiring or cable?” That’s a great question. And the answer is that it depends on what wire you use and whether you run it within a conduit or not. Since most people ask the question so that they can meet a particular desire for maximum burial depth, let’s start there. Breaking it down by how deep you bury the underground electrical wiring when you install it, we have the following options:
24-inches Deep Burial Depth
- Use direct-burial underground feeder cable at 24-inches deep (or more). You don’t need to use conduit at this depth with UF cable, however, you do need to provide PVC conduit on your vertical feeds starting at 18-inches.
18-inches Deep Burial Depth
- You can run THWN-2 conductors inside of PVC conduit at just 18-inches deep in the ground. This protects the wire from damage in the event someone digs overtop of the cable. THWN-2 is basically water-resistant THHN (Thermoplastic High Heat-resistant Nylon-coated wire)
12-inches Deep Burial Depth
- At 12-inches deep, you can run direct-burial feeder cable wire that is GFCI-protected. Protect it with PVC where it pops up at the house, garage, or shop.
6-inches Deep Burial Depth
- If you use galvanized EMT (metal electrical conduit) with individual conductors inside, you can bury it just 6-inches deep. The idea here is that the EMT can withstand a shovel or other significant potential cause of shorting the wiring.