Re: Conduit in trench
Petersonra,
2000 UPC 720.0 does allow water & sewer in the same trench!!! 720.0 Building Sewers or drainage piping of clay or materials which are not approved for use w/in a building shall not be run or laid in the same trench as the water pipes UNLESS BOTH of the following requirements are met:
(1) The bottom of the water pipe SHALL be at least 12" above the top of the sewer or drain line.
(2) the water pipe shall be placed on a solid shelf excavated at one side of the common trench w/a min. clear horizontal distance of at least 12" from the sewer or drain line.
Note: It does not say anything about A.B.S. Piping having to meet these requirements
I think that the only place you will find that it's not allowed in the same trench is in the public utilities books.
now does anybody have a good reason for not allowing water and electric in the same trench? what about rain and or ground water?