Conduit Inner Duct Transisition

Status
Not open for further replies.

billyzee

Member
I got such a fine suggestion last time that I thought of another one. Suppose I have a 4" underground pvc conduit with 2 - 1" innerduct pvc conduits. When the conduit surfaces vertically at ground level and the 1"ers continue on their way, up the side of a building for example. Does anyone have suggestions on how to plug the 4". Are there split caps with cut-outs or some foams that could accomplish this?
 
billyzee said:
I got such a fine suggestion last time that I thought of another one. Suppose I have a 4" underground pvc conduit with 2 - 1" innerduct pvc conduits. When the conduit surfaces vertically at ground level and the 1"ers continue on their way, up the side of a building for example. Does anyone have suggestions on how to plug the 4". Are there split caps with cut-outs or some foams that could accomplish this?

Raychem heat shrink boot with "fingers" and plugged, unused "fingers".

http://energy.tycoelectronics.com/index.asp?act=page&pag_id=2&prl_id=1&pls_id=353&prf_id=816&prr_id=1623

Order the components separately:

CBR-6-2-A breakout boot​
CBR-PLUG da plug...​
 
barbeer said:
BASF must have a big budget!:D

No, large companies are get that way because they watch their pennies and $'s as well. However they also believe in and obliged by their size to be a responsible corporate citizen and to do the right thing, at all times.

If you have another alternative device that is approved and not objectionable to the AHJ then please, by all means, share it.:smile:
 
weressl said:
If you have another alternative device that is approved and not objectionable to the AHJ then please, by all means, share it.:smile:

Sure, a big ole hunk of duct seal.

It's a duct, it needs sealing, I think I will use duct seal. :cool:
 