D Davebones Senior Member Location North Of Tampa Fl Jun 27, 2014 #1 Is a seal off required on both sides of a wall when a conduit leaves a Class 1 Div 2 location to a non hazardous location ?
Is a seal off required on both sides of a wall when a conduit leaves a Class 1 Div 2 location to a non hazardous location ?
G greenspark1 Senior Member Location New England Jun 27, 2014 #2 No, only one side. See NEC 501.15 (B)(2).