Conduit next to propane tank and propane pipe

Status
Not open for further replies.

Constantin

Member
Location
New Hampshire
Occupation
Master Electrician
I am looking to run a conduit to an AC compressor disconnect.
The conduit will pass behind a propane tank (less or equal to 250 Gal) and along a propane pipe for like 6 feet.

Are there any limitations or spacing requirements between an electrical conduit and propane tank/pipe?

Thank you
 
I am looking to run a conduit to an AC compressor disconnect.
The conduit will pass behind a propane tank (less or equal to 250 Gal) and along a propane pipe for like 6 feet.

Are there any limitations or spacing requirements between an electrical conduit and propane tank/pipe?

Thank you
is the area classified? If so there are some limits on what kind of conduit you need to use and some possible sealing requirements.
 
Unless you have regular open transition/ semi open transition like possibly at a dispensing/refilling station you generally don't have any Art 5XX hazardous location here. A quick connect coupling that is only used once in a while when swapping tanks usually won't trigger hazardous location requirements.
 
Unless you have regular open transition/ semi open transition like possibly at a dispensing/refilling station you generally don't have any Art 5XX hazardous location here. A quick connect coupling that is only used once in a while when swapping tanks usually won't trigger hazardous location requirements.

Yes, I think the location is not classified
I was wondering if a conduit run next to the propane tank and a propane pipe needs any spacing from them
 
Yes, I think the location is not classified
I was wondering if a conduit run next to the propane tank and a propane pipe needs any spacing from them
As long as you don't end up supporting one from the other - not really.

Could possibly have something like a unistrut channel that independently supports both at same time though.
 