Re: conduit penetrations/sleeves
Roger, I was required to install metal sleeves through a block wall when running EMT with power conductors. We were running 4" EMT, so we used 6" GRC sleeves, which had to extend 1" through each side of the wall. The sleeves were patched in with mortar, and then the conduits were fire-caulked within the sleeves. This is the spec for the plant. What would be a problem with this installation? Would this affect impedence in the equipment grounding path? The EGC system on this conduit is pretty good, with a separate EGC per 250.122, and bonding bushings on either end, per plant spec.