Under what conditions, like how long a run and wire size being pulled, do you have to do the following:
1. Use larger than code minimum conduit
2. Need to use a metal elbow in a PVC run
3. Need to use wire lubricant
4. Not pull by hand
 
A really short run you could push the wires through, at some length fish tape is needed, at a longer length lubricant is needed. I'd like some general rules to follow, or if there is a good reference I should go to that would be great.
 
I'm planning an underground run of 1/2" PVC sch 80 for a detached garage (3 14AWG THWN conductors). It is about 42 feet between elbows, which both go up to LBs. My gut feeling says this will not need lubricant or metal elbows and can be pulled by hand.
 
Is anything special needed to protect the conduit from ground movement due to frost, since it is not below the frost line? Expansion fittings on the two vertical parts?
 
Thanks in advance. I haven't said so before, but this form is great and has been a great help.
	
		
			
		
		
	
				
			1. Use larger than code minimum conduit
2. Need to use a metal elbow in a PVC run
3. Need to use wire lubricant
4. Not pull by hand
A really short run you could push the wires through, at some length fish tape is needed, at a longer length lubricant is needed. I'd like some general rules to follow, or if there is a good reference I should go to that would be great.
I'm planning an underground run of 1/2" PVC sch 80 for a detached garage (3 14AWG THWN conductors). It is about 42 feet between elbows, which both go up to LBs. My gut feeling says this will not need lubricant or metal elbows and can be pulled by hand.
Is anything special needed to protect the conduit from ground movement due to frost, since it is not below the frost line? Expansion fittings on the two vertical parts?
Thanks in advance. I haven't said so before, but this form is great and has been a great help.
 
				