Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
Yup, these boiler plate guys like to waste peoples money. As if the connections to miles of rebar in the footing weren't sufficient.I especially like Note 3. Depending on your soil conditions you might need a truck load of ground rods
Looks like they are quoting 250.52(A)(3) for a CEE. But they are showing it in the slab not the footer as would be required for the UFER.No it does not need to be in a raceway. It would be nearly impossible to damage a #3/0 or #4/0 copper conductor that is strapped to the wall. That looks like typcial overkill boiler plate stuff from the dirt worshipers. And why is there a bare conductor run in the slab?
I think Mike had a video showing that trying to get even to the 25ohm limit was over 100ft of rod and still going.I especially like Note 3. Depending on your soil conditions you might need a truck load of ground rods
Yeah, good luck complying with that one!I especially like Note 3. Depending on your soil conditions you might need a truck load of ground rods
It actually shows both connecting to the rebar and in the slab.Looks like they are quoting 250.52(A)(3) for a CEE. But they are showing it in the slab not the footer as would be required for the UFER.
Saw that, not required.It actually shows both connecting to the rebar and in the slab.
I've seen this before in commercial buildings with poured concrete construcution where they run bare copper conductors within the slab.Saw that, not required.
Had one person that did this in an attempt to sort of create an EP bond to the basement slab, not sure what for.
Which part there's a lot to choose from.Absolutely ridiculous.