Conduit Req.?

Merry Christmas

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I believe a "stub/stick" of conduit would be required when running vertical on wall but do the conductors need to be enclosed in a raceway for the entire length??

1730465022051.png
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Are you referring only to the GEC? Review 250.64(B). Securing and Protection Against Physical Damage.
If not exposed to damage it can be installed without conduit or other protection even exposed on surface. As always what constitutes "Subject to damage" is up to debate and may be at the discretion of the AHJ. (not saying it is right but lacking clear definition it is what it is.)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No it does not need to be in a raceway. It would be nearly impossible to damage a #3/0 or #4/0 copper conductor that is strapped to the wall. That looks like typcial overkill boiler plate stuff from the dirt worshipers. And why is there a bare conductor run in the slab?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I especially like Note 3. Depending on your soil conditions you might need a truck load of ground rods :)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I especially like Note 3. Depending on your soil conditions you might need a truck load of ground rods :)
Yup, these boiler plate guys like to waste peoples money. As if the connections to miles of rebar in the footing weren't sufficient. :rolleyes:
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
No it does not need to be in a raceway. It would be nearly impossible to damage a #3/0 or #4/0 copper conductor that is strapped to the wall. That looks like typcial overkill boiler plate stuff from the dirt worshipers. And why is there a bare conductor run in the slab?
Looks like they are quoting 250.52(A)(3) for a CEE. But they are showing it in the slab not the footer as would be required for the UFER.
I especially like Note 3. Depending on your soil conditions you might need a truck load of ground rods :)
I think Mike had a video showing that trying to get even to the 25ohm limit was over 100ft of rod and still going.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Looks like they are quoting 250.52(A)(3) for a CEE. But they are showing it in the slab not the footer as would be required for the UFER.
It actually shows both connecting to the rebar and in the slab.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Saw that, not required.
Had one person that did this in an attempt to sort of create an EP bond to the basement slab, not sure what for.
I've seen this before in commercial buildings with poured concrete construcution where they run bare copper conductors within the slab. :unsure:
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
To the OP be careful on your bid, there are many issues with this drawing. Note 3 requires 5 ohms ground resistance, that may not be possible. The correct way is to have the soil resistiviy tested and then design the grounding array. There are other issues such as a 3/0 to ground rods when only a 6 is required
 