Code requirements for electrical conduit crossing a gas pipe? Gas pipe is existing on the exterior a wall and the new electrical conduit is to route around the existing gas pipe.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Conduit Routing

Not a code issue, I don't see any problem with crossing but I would stay 1" away from gas line, if it is before gas meter. If after gas meter AHJ may want bonded, how to depends on what version of nec you are under. 1999 in 250.104 had a awful rule on gas piping that was removed in 2002 version.
 