I have been wiring convenience store/ fuel stations for the last 10 years, and have always put a sealoff on each end when running below the fuel dispensers.
ex. from the building to a light pole through the fuel island. Is a seal needed if I have at least 2 feet of cover (514.8 ex. 2) and is just passing below the class 1 Div 2 and not penetrating vertically through it? Just wondering because you can run pvc if it has at least 2 feet of cover and I do not believe that below 2 feet is a classified location if so I cannot locate it in the great book. Thanks for your input!
ex. from the building to a light pole through the fuel island. Is a seal needed if I have at least 2 feet of cover (514.8 ex. 2) and is just passing below the class 1 Div 2 and not penetrating vertically through it? Just wondering because you can run pvc if it has at least 2 feet of cover and I do not believe that below 2 feet is a classified location if so I cannot locate it in the great book. Thanks for your input!