conduit run

Status
Not open for further replies.
There is no set limit. It will be influenced mostly by your ability to sucessfully pull the sizes and types of conductors through the particular type and size of conduit. A cable pulling tension calculation is where you get the specific answer, for a specific situation.

Welcome to the forum.
 
In addition to what Charlie has said, you will want to check the engineers specifications. I have seen quite a few specs the require a j-box every 100 feet.

Chris
 