conduit run

Status
Not open for further replies.

raider1

Senior Member
Staff member
Location
Logan, Utah
The NEC does not have any specified distance at which a pull box must be installed in a straight run of conduit.

Many engineering specs have a distance of 100' before a pull box must be installed.

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You need a pulling point once you've reached 360 degrees of bend in the run. If the run contains less than 360 degrees worth of bends there is no limit to the length of the conduit run.
 