class1 division 2,cable is p.v.c. outer sheath does have mc written on it and a british standard number that is now faded,inner cores have varnished cambric insulation strips twisted around them,the transformer is out of the 40 metre loading radius,cable very stiff
There are still some incongruencies. Where is the facility itself located? The US? Somewhere else?
While the area classification may be documented Class I, Division 2 the cable is odd. A British Standard marking is not of particular interest, but ?steel wire? armoring is. It isn?t a recognized US domestic cable construction for the installation you described. This doesn?t at all mean it is a substandard product; only that it has not been certified to a US standard for the application. If it had been marked ?TC? though with a NRTL mark ? I wouldn?t bat an eye.
If British IP or CENELEC Standards are being used for this design or installation, as the ?
40 metre loading radius? seems to imply, it would be a classic case of attempting to ?mix and match? NEC and IEC systems. Actually, it
can be done, but it takes a great deal of experience to do it correctly ? and even then it often produces some odd results. Still safe ? but nonetheless odd and usually suspicious.
If we were permitted to assume the cable would otherwise be acceptable in Division 2, then no seal would generally be required at the transformer. If the cable were routed through or terminated in an unclassified location though, Section 501.15(E)(4) comes into play and a boundary seal would be required. This is extremely unusual for cables as opposed to conduits. The steel wire armored cable construction described is not considered to have gas/vaportight sheath because the interstices of the wire create a breach path ? even with the PVC jacket.
In the ?real? world, I don?t believe seals are necessary at all in the installation as I understand it; but that is definitely a non-authoritative opinion.