Wastewater from a couple of toilet rooms runs into a sealed pit (or burried tank), which has pumps to pump the wastewater back out.
From NFPA 820, I believe the inside of the pit should be a class 1 division 1 location. Does that sound right?
Wiring from the pumps and float switches passes through conduits to a control panel. Since the pit is Cl 1 Div 1, I specified seal-offs in the conduit runs. Those are required, right?
What does the contractor have to put inside the seal off's? Is duct seal sufficient, or is concrete required?
The electrical contractor would like to add a splice box between the seal-offs and the pit. Does the box have to be explosion proof??
Thanks in advance,
Steve
From NFPA 820, I believe the inside of the pit should be a class 1 division 1 location. Does that sound right?
Wiring from the pumps and float switches passes through conduits to a control panel. Since the pit is Cl 1 Div 1, I specified seal-offs in the conduit runs. Those are required, right?
What does the contractor have to put inside the seal off's? Is duct seal sufficient, or is concrete required?
The electrical contractor would like to add a splice box between the seal-offs and the pit. Does the box have to be explosion proof??
Thanks in advance,
Steve