Hi,
This question is in regard to an area that goes from a unclassified location to a class 1 div 2 group d (natural gas) location with conduit seals. NEC 2008 section 501.15 (B)(2) states, "Conduits shall be sealed to minimize the amount of gas or vapor....Such seals shall not be required to be explosionproof..." (We are not using "explosionproof apparatus" as our protection method. We are using I.S. and nonincendive circuits)
501.15(C) states "Class 1 Div 1 and 2 seals. Seals installed...shall comply with 501.15(C)(1) through (C)(6). (C)(6) is the 25% (or 40%) fill requirement.
However, the exception immediately below 501.15(C) states: "Exception: seals not required to be explosionproof by 501.15(B)(2) or 504.70"
Since my seals are not required to be explosionproof by (B)(2), I'd think that if 501.15(C) is a "rule" that includes the 25% fill requirement, since there is a valid exception to said rule that would mean that I do not need to abide by it.
My thoughts are that the seal is providing one or two things. Minimizing gas or vapor travel for non-explosionproof applications, and an explosionproof seal for those requiring it. I'd think that the 25% fill requirment is to ensure an explosionproof seal, whereas sealing a seal listed at 25% to, say, 50% fill is sufficient to minimizing gas or vapor travel. Or for that matter, if it is not required to be explosionproof, why couldn't I just use DUX seal?
So, to summarize, 501.15(C) states that seals for Class 1 div 1&2 shall comply with (C)(1) through (C)(6), one of which is the 25% fill requirement.
However, to me it seems that the exception immediately below it exempts me from that requirement.
Does anyone see any holes in my swiss cheese logic? the seals are already installed, although the sealing compound has not been poured, but it would be painful to replace them.
Thanks,
Ken McDonnell
This question is in regard to an area that goes from a unclassified location to a class 1 div 2 group d (natural gas) location with conduit seals. NEC 2008 section 501.15 (B)(2) states, "Conduits shall be sealed to minimize the amount of gas or vapor....Such seals shall not be required to be explosionproof..." (We are not using "explosionproof apparatus" as our protection method. We are using I.S. and nonincendive circuits)
501.15(C) states "Class 1 Div 1 and 2 seals. Seals installed...shall comply with 501.15(C)(1) through (C)(6). (C)(6) is the 25% (or 40%) fill requirement.
However, the exception immediately below 501.15(C) states: "Exception: seals not required to be explosionproof by 501.15(B)(2) or 504.70"
Since my seals are not required to be explosionproof by (B)(2), I'd think that if 501.15(C) is a "rule" that includes the 25% fill requirement, since there is a valid exception to said rule that would mean that I do not need to abide by it.
My thoughts are that the seal is providing one or two things. Minimizing gas or vapor travel for non-explosionproof applications, and an explosionproof seal for those requiring it. I'd think that the 25% fill requirment is to ensure an explosionproof seal, whereas sealing a seal listed at 25% to, say, 50% fill is sufficient to minimizing gas or vapor travel. Or for that matter, if it is not required to be explosionproof, why couldn't I just use DUX seal?
So, to summarize, 501.15(C) states that seals for Class 1 div 1&2 shall comply with (C)(1) through (C)(6), one of which is the 25% fill requirement.
However, to me it seems that the exception immediately below it exempts me from that requirement.
Does anyone see any holes in my swiss cheese logic? the seals are already installed, although the sealing compound has not been poured, but it would be painful to replace them.
Thanks,
Ken McDonnell