mioduz
Member
- Location
- Pennsylvania
- Occupation
- Controls eng
I am having a debate with a co-worker over use of seals within a Hazardous location
Facts:
Class 1 Div 2 Area
NEMA 4 Panel with Purge Controller installed to comply with Cl1 Div 2 Required Rating
The Control cabinet needs a vortec cooler installed, and I have purchased a Cl1 Div2 rated solenoid valve to control said cooler
The solendoid (red hat) has a 1/2" conduit connection and wire leads
My Co-Workers claim is that we can directly mount the solenoid to the enclosure with a short nipple and a conduit hub, without using a seal.
I disagree with this interpretation of the NEC code and state that ALL conduit entries need a seal NO MORE than 18" away from enclosure.
Can anyone shed some light on which of us is correct?