Is a conduit seal required between a Class 1 div 1 area and a Class 1 div 2 area? From what i have been reading you need a conduit seal only when exiting these areas to a unclassified area not between divisions.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
see 501.14(A)(4) and 501.15(B)(2). Both boundaries require seals.
I "liked" it, but I believe you meant 501.15(A)(4).

Is a conduit seal required between a Class 1 div 1 area and a Class 1 div 2 area? From what i have been reading you need a conduit seal only when exiting these areas to a unclassified area not between divisions.
See the first sentence in each Section Don mentioned. Every boundary crossing requires a seal, even between Classes and Divisions.
 

Hustlle2022

Member
Location
Mississippi
Occupation
Electrician
So my understanding of the above would be the seal would be placed on the Div 2 side conduit leaving the hazardous area to a non hazardous area?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
So my understanding of the above would be the seal would be placed on the Div 2 side conduit leaving the hazardous area to a non hazardous area?
Your original question was, “Is a conduit seal required between a Class 1 div 1 area and a Class 1 div 2 area?”
What does Section 501.15(A)(4) tell you?
 

Hustlle2022

Member
Location
Mississippi
Occupation
Electrician
My interpretation is the wiring method and seal is extended into the div 2 side, so the seal would be installed on the div 2 side of conduit.

Where seals are required for boundary conditions as defined
in 501.15(A)(4), the Division 1 wiring method shall extend into
the Division 2 area to the seal, which shall be located on the
Division 2 side of the Division 1–Division 2 boundary
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
My interpretation is the wiring method and seal is extended into the div 2 side, so the seal would be installed on the div 2 side of conduit.

Where seals are required for boundary conditions as defined
in 501.15(A)(4), the Division 1 wiring method shall extend into
the Division 2 area to the seal, which shall be located on the
Division 2 side of the Division 1–Division 2 boundary
And then another seal on the unclassified side of the Div2/Unclassified boundary.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
The answer to your initial question is, “Yes, a conduit seal is required between a Class I, Division 1 location and a Class I, Division 2 location.” So, where does the “non hazardous area” you mentioned in Post #4 even enter the discussion?
 