Conduit Seals in Class I, Division 1, Group B

Status
Not open for further replies.

Dale001289

Senior Member
Location
Georgia
Back in the 'good ol days', we used to have to installconduit seals within 1.5” of the arcing device in Class I Division1 Group B environments – we therefore omitted the associated conduit union, usually a C-H UNY.
Ican’t find any support for this in NEC. Comments?

 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
If you go back far enough and deep enough, you will most likely find it was a listing issue. [Section 110.3(B)]
 

Dale001289

Senior Member
Location
Georgia
If you go back far enough and deep enough, you will most likely find it was a listing issue. [Section 110.3(B)]

I would say that's correct Bob. I was just reviewing Crouse Hinds Catalog. The 1.5" requirement for sealing in Division 1, Group B is shown for 'EDS/EFS Series Control Stations' and a few other areas, in fine print.

Thanks
 