My question concerns the specific language of the Article 3XX.30 sections of the 2002 NEC. For all the conduit and raceway systems, the code states; "shall be securely fastened within X mm (x ft) of each outlet box, junction box, device box, cabinet, conduit body, or other tubing termination."
Under the cabling methods, the same section specfically mentions "fitting." (334.30)
With that in mind, suppose you have a run of EMT conduit that is installed parallel to a large cabinet of panelboard. The conduit terminates near the bottom of the panel, but is run along the length of the side of the equipment. According to the language, I could secure the conduit 3 feet above the panel and would be compliant, even though there may be another 2'11" of remaining conduit to the actual termination.
I am not trying to beat the code or actually get away with this, but I think it is interesting that the word fitting is not used in these sections. I know the codes intent is a linear length from termination and not proximity location from any raceway point to the enclosure point, but there is the potential of this being abused. Any thoughts?
Under the cabling methods, the same section specfically mentions "fitting." (334.30)
With that in mind, suppose you have a run of EMT conduit that is installed parallel to a large cabinet of panelboard. The conduit terminates near the bottom of the panel, but is run along the length of the side of the equipment. According to the language, I could secure the conduit 3 feet above the panel and would be compliant, even though there may be another 2'11" of remaining conduit to the actual termination.
I am not trying to beat the code or actually get away with this, but I think it is interesting that the word fitting is not used in these sections. I know the codes intent is a linear length from termination and not proximity location from any raceway point to the enclosure point, but there is the potential of this being abused. Any thoughts?