Re: Conduit size in classified area
This most likely comes from a misunderstanding of [2005] 501.15(C)(6) or [2002] 501.5(C)(6).
The restriction is on seal fittings not the conduits themselves. Since it was originally introduced in the 1996 NEC, most manufactures now have their seal fitting certified for 40% fill of RMC. In the 2002 NEC it was clarified the fill restriction was based on RMC since other forms of raceways now recognize they may have different internal diameters (I.D.)
Edit: Corrected reference from 1999 NEC to 1996 NEC (I should have remembered - I wrote that Proposal)
[ September 14, 2005, 12:08 PM: Message edited by: rbalex ]