Have a Communications Equipment Ground conductor passing through metal EMT between 3 to 10ft (conduit length). Conduit is being used to support / protect the ground wire. Is this EMT required to be bonded on both ends?
With such short pieces of metal sleeve used, I cannot see how this would still require bonding. NEC 250.86 Exception #2 states that short sections of metal raceway used to provide protection or support shall not be required to be connected to the GEC. NEC 300.10 Exception #1 states the same thing.
Thanks
Thanks