conduit straps
neenah
Is it a code violation attach conduits together together using back to back mineralac straps. The conduit in question is securely mounted. If this is a violation could you give me a code referance.
Thanks,
Troy
300.11 Securing and Supporting.
(B) Raceways Used as Means of Support. Raceways shall only be used as a means of support for other raceways, cables, or nonelectric equipment under the following conditions:
(1) Where the raceway or means of support is identified for the purpose; or
(2) Where the raceway contains power supply conductors for electrically controlled equipment and is used to support Class 2 circuit conductors or cables that are solely for the purpose of connection to the equipment control circuits; or
(3) Where the raceway is used to support boxes or conduit bodies in accordance with 314.23 or to support luminaires (fixtures) in accordance with 410.16(F)
Conduit Support
Conduit Support
Thanks for the help. Now I will look up these code references and see how it applies to my situation. I'm also a big Clint fan! Thanks again.
Troy
If the raceways have properly spaced supports, can you use back to back minerallac's as additional bracing?
When I first read this post with Bob's resoponse, I thought it would be the first 2 post thread ever. I guess not.
TKB, I'd say that taken exactly as the nec reads, no.