E EEC Senior Member Location Maryland Aug 7, 2008 #1 Does the NEC require bonding conduit stub-ups when the stub-up is not terminated into box with locknuts?
Does the NEC require bonding conduit stub-ups when the stub-up is not terminated into box with locknuts?
George Stolz Moderator Staff member Location Windsor, CO NEC: 2017 Occupation Service Manager Aug 7, 2008 #2 Depends on the particulars. See 250.86, paying attention to the exceptions.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Aug 8, 2008 #3 If the raceway stub-up is metallic it must always be bonded by some method.