New member
I'm having trouble understanding section 348-13.
This section is for EMT supports.
The section states that emt should be supported every 10 ft and within 3 ft of boxes, panels, condulets and tubing terminations. What are tubing terminations.

kunsamii
 
Re: conduit support

A termination is just the end of a conduit.

This could be a conduit that just ends with a bushing, no box, typical for Voice and Data conduits.
 