jvee1985

Member
Location
Kansas
does anyone have advice on supporting 3/4 inch EMT conduit to a finished sheet rocked ceilings without finding rafters. Can one use toggle bolts?
 

Riograndeelectric

Senior Member
EZ anchors work quite well in drywall




Specified for anchorage into Gypsum Wallboard

http://www.smithfast.com/ezanc.htm

The E-Z ANCOR? is a one-piece self-drilling anchor designed for optimal holding performance in gypsum wallboard.

Available in zinc or high strength engineered plastic (non conductive).

They are the ideal anchors for 3/8, 1/2 and 5/8 inch gypsum wallboard.
 

celtic

Senior Member
Location
NJ
The best thing to do would be hang a piece of strut from the two joists.

3" Strut, 3/8" hardware for 1(one) - 3/4" EMT
icon14.gif


BTW, who is paying for this engineering marvel?
marvelfirestone.jpg
 

buddhakii

Senior Member
Location
Littleton, CO
EZ anchors work quite well in drywall




Specified for anchorage into Gypsum Wallboard

http://www.smithfast.com/ezanc.htm

The E-Z ANCOR? is a one-piece self-drilling anchor designed for optimal holding performance in gypsum wallboard.

Available in zinc or high strength engineered plastic (non conductive).

They are the ideal anchors for 3/8, 1/2 and 5/8 inch gypsum wallboard.

I think it say right on the package that they are not to be used to suspend from the ceiling.
 

barbeer

Senior Member
Toggles can be acceptable, but make sure they will bare the weight of what you are installing. I would not be as concerned with the 3/4 emt but whats inside of that raceway.
 

LJSMITH1

Senior Member
Location
Stratford, CT
Based on UL2239's specification for straps and hangars, a 3/4" EMT strap needs to support a minimum of 100 lbs. However, manufacturers are required to guarantee 3x safety load ratings for the straps/hangars.

There are toggle bolts that will easily support 100lbs, but that is entirely reliant on the strength of the wallboard. The wallboard is the primary issue, not so much the fastener.

If this were my installation, I would find the joists and use 2" screws to attach the straps. In instances where the EMT runs parallel with the joists in places, I would use pieces of unistrut or 5/8' x 1.5" wood to bridge the joists throughout the run. It may not look pretty, but at least you are not relying on paper and gypsum to hold up your raceway.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
By the time you make a 1/2" hole or so large enough for the toggle, your one hole strap will almost suck through it when you tighten it up. I would definitely try to find a rafter, or span with strut.
 

stevenje

Senior Member
Location
Yachats Oregon
"By the time you make a 1/2" hole or so large enough for the toggle, your one hole strap will almost suck through it when you tighten it up. I would definitely try to find a rafter, or span with strut."

If you install a fender washer between the strap and the drywall, the EMT one- hole strap will not suck into the hole that toggle bolt requires.
 

luckyshadow

Senior Member
Location
Maryland
the question is what type of environment ?
Prison , church classroom, high school age kids, open to the general public?

Would there be any abuse to the conduit run?

I personally have probably run tens of thousands of feet of 3/4 on sheetrock ceilings with toggle bolts using both minnies and 1 hole bands. I bought a hole saw just big enough for a toggle wing to fit through and used fender washer behind the strap like stevenje said.
 
Last edited:

iaov

Senior Member
Location
Rhinelander WI
Unistrut between the studs if you realy don't want it going anywhere. Not so much a Modern Marvel as a safe, neat and workman like install!!
 

iwire

Moderator
Staff member
Location
Massachusetts
Unistrut between the studs if you realy don't want it going anywhere. Not so much a Modern Marvel as a safe, neat and workman like install!!

Neat?

I guess that would depend on where it's being run, EMT surface mounted on a Sheetrock ceiling is ugly enough, seeing 18" of uninstrut every ten feet to support just one single 3/4" EMT is going to look awful.
 

iaov

Senior Member
Location
Rhinelander WI
Those probably would look better. My wife says shes on your side on this and there is no way to make EMT across a cieling look good.:smile:
 